Discuss issues and ideas you have to configuring displays with PowerVision
Roger Miauton
Posts: 4
Joined: Mon May 26, 2014 12:26 pm

ModbusTCP Client PV780T

Post by Roger Miauton » Fri Sep 01, 2017 1:51 am

Hello,
i want set up a ModbusTCP Client with an USB-Ethernet adapter on the PV780T. Is this generally possible or do i have to use the serial(RS485) port?
I made a Modbus Device setup with two Remote Servers and i try to send out the registers with the function "start refreshing mapping group".
Is this the only way to send out registers, which function should i use?
Which ipAdress should i give the USB-Ethernet adapter, fix Address or DHCP?

Thanks a lot for your Help.
Johannes
boyce
Enovation Controls Development
Enovation Controls Development
Posts: 322
Joined: Wed Sep 08, 2010 5:09 pm

Re: ModbusTCP Client PV780T

Post by boyce » Fri Sep 01, 2017 11:15 am

Here are some screen shots for configuring ModbusTCP. I've not done it before so this information is from the test engineers. The screen shots show the PowerVision configuration and configuring Mdbus on the PC. From what they tell me the PC firewall configuration may have to be changed to allow the connection. You probably will have to download the pdf files to get a better look at them.
modbustcp1.JPG
modbustcp1.JPG (101.4 KiB) Viewed 146 times
modbustcp2.JPG
modbustcp2.JPG (95.95 KiB) Viewed 146 times
Modbus TCP Client-Master - PV780 - 2.7.10291.pdf
(514.42 KiB) Downloaded 19 times
Modbus TCP Server-Slave - PV780 - 2.7.10291.pdf
(434.96 KiB) Downloaded 13 times
Boyce Schrack
Enovation Controls
Roger Miauton
Posts: 4
Joined: Mon May 26, 2014 12:26 pm

Re: ModbusTCP Client PV780T

Post by Roger Miauton » Mon Sep 04, 2017 6:28 am

Thanks for your answer.
I tried your settings with a Modbus-PC-slave (server) but i got the server-communication-status 0x81 back. What means this, where can i decode the state?
Maybe its helpful if i use the same Modbus-server, do you have a download link for the TCP.Slave.cfg?

Thank you.
boyce
Enovation Controls Development
Enovation Controls Development
Posts: 322
Joined: Wed Sep 08, 2010 5:09 pm

Re: ModbusTCP Client PV780T

Post by boyce » Tue Sep 05, 2017 8:47 am

The 0x81 is a NO CONNECTION. Here is a document with the exception and status codes and the Mdbus configuration files.
TCPMaste.zip
(395 Bytes) Downloaded 17 times
TCPSlave.zip
(396 Bytes) Downloaded 18 times
Boyce Schrack
Enovation Controls
alb
Posts: 43
Joined: Wed Dec 15, 2010 1:30 pm

Re: ModbusTCP Client PV780T

Post by alb » Tue Jan 02, 2018 4:47 pm

Does ModbusTCP rely on the USB Ethernet dongle?
boyce
Enovation Controls Development
Enovation Controls Development
Posts: 322
Joined: Wed Sep 08, 2010 5:09 pm

Re: ModbusTCP Client PV780T

Post by boyce » Fri Jan 05, 2018 9:05 am

Yes, on a PV780T ModbusTCP uses the USB Ethernet dongle.
Boyce Schrack
Enovation Controls