Hi
There is a serial port on the HV700, in Powerview 2.3 setup up page there is an option to set the Protocol as "None (Raw Serial)"
How do you use this i.e. how do you send data either from a Script or State Engine
I cant find this documented anywhere, are there any sample configs?
Regards, Brian
Serial Port
- BrianM
- Posts: 8
- Joined: Thu Sep 27, 2012 10:51 am
- BrianM
- Posts: 8
- Joined: Thu Sep 27, 2012 10:51 am
Re: Serial Port
Bump
Anybody?
Anybody?
- jedwards
- Enovation Controls Development
- Posts: 16
- Joined: Fri Jul 30, 2010 8:24 am
Re: Serial Port
At the moment, the serial port in None mode is essentially off. There is not currently an API mechanism to write or read from the serial port. The only user available API would be to use the MODBUS protocol with the serial port.
- BrianM
- Posts: 8
- Joined: Thu Sep 27, 2012 10:51 am
Re: Serial Port
Thank you