DM3 Function on PV750

Discuss issues and ideas you have to configuring displays with PowerVision
tshiii
Posts: 79
Joined: Thu Sep 09, 2010 8:56 pm

DM3 Function on PV750

Post by tshiii » Mon Apr 16, 2012 3:27 am

Dear Sir or Madam,

Would you please advise me if DM3 (Diagnostic Data Clear) function can be used on PV750? If so, please also advise me how to set by configuration tool.

Thank you and best regards,

Shiii
ksaenz
Enovation Controls Development
Enovation Controls Development
Posts: 263
Joined: Thu Aug 19, 2010 7:53 am

Re: DM3 Function on PV750

Post by ksaenz » Mon Apr 16, 2012 3:37 pm

Hello Shiii,

DM3 can be easily used on the PV750, it is just a request for PGN 65228 (0xFECC) and you can do that with a Free Form CAN message like in the attached screenshot.

The CAN message will look like this:
0x18EA00F2 CC FE 00

Regards,

ksaenz
Attachments
DM3.PNG
DM3.PNG (22.25 KiB) Viewed 138 times
tshiii
Posts: 79
Joined: Thu Sep 09, 2010 8:56 pm

Re: DM3 Function on PV750

Post by tshiii » Tue Apr 17, 2012 4:22 am

Hello Ksaenz,

Thank you for your prompt attention and the information.

If I need to broadcast(output) some data via CAN-Bus, how should I set on the configuration tool? Some example as well as the DM3 below would be very helpful for me to understand how to set.

Best regards,
Shiii
ksaenz
Enovation Controls Development
Enovation Controls Development
Posts: 263
Joined: Thu Aug 19, 2010 7:53 am

Re: DM3 Function on PV750

Post by ksaenz » Tue Apr 17, 2012 8:13 am

tshiii,

If you want to broadcast standard J1939 parameters you can simply add them to the Transmit Device under the desired CANPort in Environment Setup and the PV750 will use the PGN, scaling, and repetition rate specified in the J1939 Parameters table found in the Database section.

If you want to broadcast other CAN messages like the DM3 request in the attached example you can set them up as Free Form CAN messages. In this case you have to specify the Message Type, Frame ID, Data Length, filters (if used), and the data in the message manually. To send Free Form CAN messages you use actions in state machines.

Regards,

ksaenz
Attachments
DM3 request.zip
PV750 configuration created with PVCS 2.3.11157
(115.55 KiB) Downloaded 25 times
tshiii
Posts: 79
Joined: Thu Sep 09, 2010 8:56 pm

Re: DM3 Function on PV750

Post by tshiii » Wed Apr 18, 2012 3:04 am

Dear Ksaenz,

Thank you for the information and kind support. If any further questions arise, will let you know.

Thank you and best regards,
Shiii