Hello,
I am trying to list active diagnostic messages on a table. I am aware that on version 780 there is a table for DM2. However when I send a diagnostic message,some --FECA-- message using a CAN bus, while a pop-up appears showing information about the message, Engine Diagnostics table warns as " Timeout! No response from sources.".
Open to any help. Thanks in advance.
DM1 Listing
- serhatovan
- Posts: 5
- Joined: Fri Sep 02, 2016 9:14 am
- stalley
- Enovation Controls Development
- Posts: 618
- Joined: Tue Mar 18, 2014 12:57 pm
Re: DM1 Listing
Hello serhatovan,
I am assuming you are using a standard configuration from PowerVision Configuration Studio 2.8 patch 3 (2.8.10546).
When a user navigates to the Engine Diagnostics page, the display sends a request for the DM2s. DM2s/xFECB are the previously active faults. If the device (usually the engine ECU) responds, the table will be populated with faults that are no longer active. A history of faults, you could say.
The currently active faults are shown in the overlay that pops up when a new active fault is received. If the display is receiving any active (DM1/xFECA), the overlay is shown until the fault is acknowleged by pressing the button near the Hide text. When all faults have been acknowleged and the display is still receiving active faults, the overlay will be hidden and the button text will change to Recall.
The display must receive the xFECA at a 1Hz rate for a fault to stay active.
If you want the DM1s displayed in a table instead of the overlay, you will need to customize your configuration.
I am assuming you are using a standard configuration from PowerVision Configuration Studio 2.8 patch 3 (2.8.10546).
When a user navigates to the Engine Diagnostics page, the display sends a request for the DM2s. DM2s/xFECB are the previously active faults. If the device (usually the engine ECU) responds, the table will be populated with faults that are no longer active. A history of faults, you could say.
The currently active faults are shown in the overlay that pops up when a new active fault is received. If the display is receiving any active (DM1/xFECA), the overlay is shown until the fault is acknowleged by pressing the button near the Hide text. When all faults have been acknowleged and the display is still receiving active faults, the overlay will be hidden and the button text will change to Recall.
The display must receive the xFECA at a 1Hz rate for a fault to stay active.
If you want the DM1s displayed in a table instead of the overlay, you will need to customize your configuration.
Sara Talley
Software Engineer
Enovation Controls
Software Engineer
Enovation Controls
- serhatovan
- Posts: 5
- Joined: Fri Sep 02, 2016 9:14 am
Re: DM1 Listing
Thank you Sara